I can't download an HMI to an IPC. Everytime that i try it i get the same error:
The IPC is configured as TARGET_MODE=HMI
Versions: CPS5.1.0 - IPC 5.1 - HMI 5.1.1
What can be wrong?
Thasnks in advance
Hi comunity,
I can't download an HMI to an IPC. Everytime that i try it i get the same error:
The IPC is configured as TARGET_MODE=HMI
Versions: CPS5.1.0 - IPC 5.1 - HMI 5.1.1
What can be wrong?
Thasnks in advance
You have to install certificate to target system.
After your unsuccessful connection you should find created certificate in C:\NexeedLocal\Certificates\RAT.Server\pkiserver\rejected. If I remember correctly the name of file should contain Bosch name of your computer. Move this file to C:\NexeedLocal\Certificates\RAT.Server\pkiserver\trusted\certs and try to deploy the IPC again. It should work.
Whole procedure is described in OES help. Look into section Project Creation > Target Systems > Activating the Control plus Studio certificate on the target system.